[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Problem adding Radiant Cooling Panel





Hi guys ,

I hope you are all doing well .

I'm adding ceiling radiant cooling panels the 5 zones I have . I keep getting this error :


** Severe  ** Node Connection Error, Node="RAD_PANEL_ZONE1_OUTLET", Inlet node did not find an appropriate matching "outlet" node.

   **   ~~~   ** If this is an outdoor air inlet node, it must be listed in an OutdoorAir:Node or OutdoorAir:NodeList object.

   **   ~~~   ** Reference Object=CONNECTOR:MIXER, Name=CW_MIXER_D

I've added the radiant panels the following way :

from Zone HVAC Radiative/Convective Units , I added ZoneHVAC:LowTemperatureRadiant:ConstantFlow

where for zone 1 it has inlet node name :rad_panel_zone1_inlet and outlet node name :rad_panel_zone1_outlet

then I've linked it with the cooling water loop (demand side of plant loop) by adding each panel to a branch using same inlet and outlet nodes .

Whats the problem ?

Please help

Thanks in advance




__._,_.___

Posted by: a.aelhefni@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___