[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] AirConditioner:VariableRefrigerantFlow: COP in Html report





TotPower = TUParasiticPower + TUFanPower + ElecHeatingPower + ElecCoolingPower + CrankCaseHeaterPower + EvapCondPumpElecPower + DefrostPower;

On 7/27/2015 8:40 AM, Richard Raustad RRaustad@xxxxxxxxxxxx [EnergyPlus_Support] wrote:
These equations should be in the Engineering Reference document.

OperatingCoolingCOP = (TotalCoolingCapacity ) / (ElecCoolingPower + CrankCaseHeaterPower + EvapCondPumpElecPower + DefrostPower );
OperatingHeatingCOP = (TotalHeatingCapacity ) / (ElecHeatingPower + CrankCaseHeaterPower + EvapCondPumpElecPower + DefrostPower );
OperatingCOP = ( TUCoolingLoad + TUHeatingLoad ) / TotPower;


On 7/27/2015 8:33 AM, Jim Dirkes jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx [EnergyPlus_Support] wrote:
I have reported COP occasionally and confess that I don't understand how it gets calculated.
You might report capacity and also power for each timestep, however, and then calculate COP 

On Mon, Jul 27, 2015 at 8:03 AM, Javed Iqbal eee.javed@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 
Hello,

Is there a way to validate COP (w/w) input in "AirConditioner:VariableRefrigerantFlow" EnergyPlus object. Though I can find  "HVAC,Average ,VRF Heat Pump Cooling COP []" output variable to check COP number. any suggestions??

Thanks in advance!

--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 








--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Life is not easy.  It’s never been easy. Expecting it to be easy is not a healthy attitude.
Relax. Refresh. Regroup. Carry on.


-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/

-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/


__._,_.___

Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___