Dear Francesco,
At first I thought you had missed an object, but it appears you are correct (as usual).
As I think about it, I can see benefits from a VAV chilled beam system for unoccupied or lightly occupied periods.  
On the other hand, I think that these "active" chilled beams may need the primary airflow in order to induce enough secondary air to achieve their rated capacity.  Of course, the primary airflow is generally small since it is only the minimum needed for people. That means the energy needed for individual rooms is relatively small compared to VAV + reheat.
Is your question related to an actual design for VAV chilled beams?  If so, does each beam have a modulating damper? Controlled by what signal? 
It would be interesting to me to understand the design rationale for reducing the primary airflow.

On Sun, Aug 30, 2015 at 6:05 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Good question. I know DesignBuilder had this restriction. Perhaps it was required at the time. Things may have changed as there have been two releases 8.2 and 8.3 since that time. I would ask at the helpdesk.

2015-08-30 11:48 GMT+02:00 fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Is modeling cooled beams connected with an air system with variable velocity (VAV) possible? 

It seems that the object AirTerminal:SingleDuct:ConstantVolume:CooledBeam can be connected only with a constant velocity system (CAV).

Regards

Francesco





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

The body must be given a little less than it needs. Otherwise it will turn traitor.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___