Schedules can be manipulated at run time by EMS.
ÂThe DesignBuilder help has some ideas on how to customise the basic E+ economiser and HR functions. You may find it useful:
Â
http://www.designbuilder.co.uk/helpv4.5/#Generic_AHU.htm
Â
Search the page for "Heat recovery control tips"
Â
Andy
Â
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, November 13, 2015 11:41 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Problem in using EMS actuator to control Controller:OutdoorAir [2 Attachments]Â
Â
Dear all,
I'm trying to model a simple CAV with a heatexchanger:airtoair and without heating coils to bring fresh air to a zone. I would also to implement freecoling for the system using the object Controller:OutdoorAir.
In this object I have to set the economizer minimum and maximum limit dbt.
The heating SPtemperature is 20 and the cooling SPtemperature is 23 extended for the whole year. At the moment I set:
Controller:OutdoorAir,
   Circuito ad Aria UTA Controllore Aria Esterna, !- Name
   Circuito ad Aria UTA Relief Air Outlet, !- Relief Air Outlet Node Name
   Circuito ad Aria UTA Ventilatore di Estrazione Air Outlet Node, !- Return Air Node Name
   Circuito ad Aria UTA Mixed Air Outlet, !- Mixed Air Node Name
   Circuito ad Aria UTA Outdoor Air Inlet, !- Actuator Node Name
   autosize,               !- Minimum Outdoor Air Flow Rate {m3/s}
   autosize,      &nbs p;        !- Maximum Outdoor Air Flow Rate {m3/s}
   FixedDryBulb,           !- Economizer Control Type
   MinimumFlowWithBypass,  !- Economizer Control Action Type
   23,                     !- Economizer Maximum Limit Dry-Bulb Temperature {C}
   ,                       !- Economizer Maximum Limit Enthalpy {J/kg}
   ,                       !- Economizer Maximum Limit Dewpoint Temperature {C}
   ,      & nbsp;&nb sp;               !- Electronic Enthalpy Limit Curve Name
   16,                     !- Economizer Minimum Limit Dry-Bulb Temperature {C}
   LockoutWithCompressor,  !- Lockout Type
   FixedMinimum,           !- Minimum Limit Type
   2,                      !- Minimum Outdoor Air Schedule Name
   ,                       !- Minimum Fraction of Outdoor Air Schedule Name
   ,    & nbsp;&nb sp;                 !- Maximum Fraction of Outdoor Air Schedule Name
   ,                       !- Mechanical Ventilation Controller Name
   ,       !- Time of Day Economizer Control Schedule Name
   No,                     !- High Humidity Control
   ,                       !- Humidistat Control Zone Name
   1,                    & nbsp;&nb sp; !- High Humidity Outdoor Air Flow Ratio
   Yes,                    !- Control High Indoor Humidity Based on Outdoor Humidity Ratio
   BypassWhenWithinEconomizerLimits; !- Heat Recovery Bypass Control TypeÂ
But in this case I obtain that in winter the heatexchanger is bypassed when external temperature are in the raneg 16-20C and it's not correct.
Â
I was wondering about how to assign different !- Economizer Minimum Limit Dry-Bulb Temperature {C} according to the season, using in this case 20C instead of 16C... and I tryed to set up a EMS actuator for the variable !- Economizer Minimum Limit Dry-Bulb Temperature {C} but things are not working. I have problems to set the actuator for that variable.
Â
Could anyone help me or point me a different solution to reach my intent?
Thanks a lot
(this message correct a the previous one)
__._,_.___
Posted by: Jean Marais <jeannieboef@xxxxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.