Tilak,
I think that you are correct: infiltration is unintended and uncontrolled.  Ventilation is intended and controlled.

Within EnergyPlus, infiltration can be specified as a constant value, but it can also be specified to vary with wind speed or occupancy.  Inherently, the heating / cooling load from infiltration is a zone load.

Ventilation, on the other hand, is delivered through an air loop and dependent on the air loop's function. Inherently, the heating / cooling load from ventilation is a system load.



On Thu, Nov 26, 2015 at 4:08 AM, fati_tilak@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi, Would you please help me to understand the different between ventilation and infiltration.

 in my case study, I want to model one residential zone which has some windows with an opening schedule for being open or closed.  I think for simple modeling the effects of outdoor air flow , I should fill" Zone infiltration: design flow rate" or " Zone infiltration: Effective Leakage Area" and "Zone Ventilation: Design flow rate". Am I right? 

I am a little confused since one of my friend advised me to fill just "Zone infiltration: design flow rate" and increase the amount of ACH.

As far as I understand Infiltration is for considering the effects of unintended flow and Ventilation is for considering the effects of purposeful flow from outside ( to provide non-mechanical cooling). So I think for considering the effects of purposeful windows opening , I should fill Ventilation object. But I am not sure. 

Thanks in advance for your time and great help.

Tilak


 




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Love is the bridge over which Truth travels 



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___