Sounds like a pointless exercise to me.  Unless you have a chilled water coil, at high chilled water temperature, there is probably no such thing as a sensible only system.  Yes, you can do it with 60 degree chilled water as long as the mixed air dewpoint is below 60, but why bother with that approach?  The coil is going to be larger than with a lower coil temperature and cost more.  So why sensible only?

If it's a normal DX coil, it's going to have both sensible and latent capacity.

And sizing only for the latent load is going to get you quite a bit of sensible capacity unless you are in a very dry climate, at which point a system sized for sensible load will almost certainly meet your latent needs.

I'm curious... Why would you take such an approach?


Robert Wichert P.Eng. LEED AP BD&C
HERS I/II     CEPE     CEA
BPI CERTIFIED SF/MF   GREEN POINT RATER
+1 916 966 9060
FAX +1 916 966 9068







===============================================
On 1/2/2016 7:11 AM, alyelhefni@xxxxxxxxx [EnergyPlus_Support] wrote:
 

hi all ,


I want to size my main system to fulfill all of the latent load and the rest of sensible load not met by this system should be met by another parallel system .

How is that possible from the point of view of sizing and design day .




__._,_.___

Posted by: RobertWichert <robert@xxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___