Sounds like a pointless exercise to me. Unless you have a chilled water coil, at high chilled water temperature, there is probably no such thing as a sensible only system. Yes, you can do it with 60 degree chilled water as long as the mixed air dewpoint is below 60, but why bother with that approach? The coil is going to be larger than with a lower coil temperature and cost more. So why sensible only? If it's a normal DX coil, it's going to have both sensible and latent capacity. And sizing only for the latent load is going to get you quite a bit of sensible capacity unless you are in a very dry climate, at which point a system sized for sensible load will almost certainly meet your latent needs. I'm curious... Why would you take such an approach? Robert Wichert P.Eng. LEED AP BD&C HERS I/II CEPE CEA BPI CERTIFIED SF/MF GREEN POINT RATER +1 916 966 9060 FAX +1 916 966 9068 =============================================== On 1/2/2016 7:11 AM,
alyelhefni@xxxxxxxxx [EnergyPlus_Support] wrote:
__._,_.___ Posted by: RobertWichert <robert@xxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |