Re: [EnergyPlus_Support] sizing to latent load only





I think it best to size the system (sizing:system) on VentilationRequirement. In the zone (sizing:zone) enter the supply air design humidity for the heating and cooling case. Don't forget that you'll need also a humidistat in the zone. Use setpointmanager:(for humidity as well as one for temperature) and assign it to place it at the appropriate node in the AHU (like after the coil).

Background: sizing:system fixes the design airflow volume rate of the system. The latent load is then calculated at the zone based on the zone moisture balance and includes supply temperature air humidity (for sizing this will be the design supply temp and humidity), moisture from sources and sinks, exhaust air temperature and humidity (zone setpoint).

I believe the coil will then size correctly. Please anyone correct me if this is not so.

On 2 Jan 2016 4:11 pm, "alyelhefni@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

hi all ,


I want to size my main system to fulfill all of the latent load and the rest of sensible load not met by this system should be met by another parallel system .

How is that possible from the point of view of sizing and design day .



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___