[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] TABS-Thermally-Active Building System [1 Attachment]





Dear Group, 

I am looking to model a "thermally active building system". The plant is a ground source heat exchanger. I am told that they will use the floor for both the heating and cooling loops.  When setting up the model in Design Builder I can only add a chilled ceiling and heated floor. Since the floors and ceilings are inverse of each other, it seemed that this would have been workable- however it seems that the model will not run because a surface can not have more than one loop. 

   ..... Last severe error=Interzone surface 4THFLOOR:ZONE1_CEILING_1_0_0 is referenced by more than one radiant system--this is not allowed
   ************* Warning:  Node connection errors not checked - most system input has not been read (see previous warning).
   ************* Fatal error -- final processing.  Program exited before simulations began.  See previous error messages.

This leaves me to wonder if it is possible to use the ground source heat pump for both heating or cooling so that there is only a single loop that changes from heating to cooling mode on a schedule.  Perhaps there is a way in Design Builder, but so far I have not found a way..  Currently the only thing I can think of is two models (one for heating and one for cooling) but would rather have a single model for obvious reasons. 

Thanks for any suggestions- file attached and system description below. 
â?? 

â??TABS-Thermally-Active Building Systemâ?? (TABS acc. to ISO 11855-1) is based on the thermal storage capacity of parts of a building. The â??Activeâ?? element of a combined heating and/or cooling system is achieved by embedding pipes in the structural concrete slabs of the building. TABS operate at temperatures close to ambient which facilitates the integration of renewable energy and cooling sources that are free of cost. Concrete floors and ceilings can be used for the heating and/or cooling of buildings.

Water temperatures for heating and cooling on active slabs:

Summer mode: water regime: 20 ° C to 22°C

Winter operation: water regime: 22 ° C to 24 ° C



Inline image 1


â??

â??â??
Jeremiah D. Crossett
 
 | Applications Engineer III  | LEED Green Associate 
â??â??
7409 SW Capitol Highway #204 | Portland, OR 97219 
â??â??
 | Direct 503-688-8951
  


__._,_.___
View attachments on the web

Posted by: Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___
Attachment not found:
D:\Eudora\Attach\Boggio.idf