Thanks all for your replies.
The keyword is “Ratio of Frame-Edge Glass Conductance to Center-Of-Glass Conductance” and is defined in the WindowProperty:FrameAndDivider object. Christopher Jones,
P.Eng.
WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
There's a field for...it's late after a 14 hour grind...something like the ratio of U-frame to U-edge...memory is just not working, sorry. It's always greater than 1 (usually around 1.2) and takes care of the thermal break from CoG to Frame. WINDOW calculates
it for it's IDF output. On 19 Feb 2016 1:55 pm, "'Jones, Christopher'
Christopher.r.Jones@xxxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
I am used to the overall window U-factor being calculated from three areas of the window � frame U-factor, edge U-factor and COG U-factor. The area weighted average of these three factors calculates the overall window
U-factor. EnergyPlus has inputs for frame U-factor and glass U-factor. How does the edge U-factor fit into the picture?
Christopher Jones,
P.Eng.
WSP Canada Inc.
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4
From:
EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Dear Edward
Thank you for your suggestion.
Hossein
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received. WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership __._,_.___ Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |