|
Ned, others, There are two effects going on with R-19 insulation between metal studs: 1) compression of R-19 insulation within the 3.5" cavity, thus reducing its R-value to 18 2) 2-D heat flow due to the metal studs, which is a much bigger effect with the studs acting like radiator fins. I don't have an exact number in my head, but I recall that the net effect was to degrade the R-value by a huge amount, like 30-40%. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 205A Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx http://weather.whiteboxtechnologies.com for simulation-ready weather data (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 2/25/2016 7:39 AM, 'Edward G. Lyon'
eglyon@xxxxxxx [EnergyPlus_Support] wrote:
__._,_.___ Posted by: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |