Hi, Yes you can have both baseboards and ptacs in the zone. Check your sizing zone objects: you should only have ONE per zone. If you do already have only one per zone, then it's likely a problem of the name of your sizing zone objects: they should be unique. Maybe the ":" isn't being read correctly in which case you have replace it by a dash "-" Best, Julien Envoyé de mon iPhone Le 2 mars 2016 à 23:47, "alvand_eng@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien Marrec <julien.marrec@xxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |