[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Energy Management System (EMS)- PTHP consumption output





Couldn't you do the same thing with a "custom meter"?

At 04:07 AM 3/4/2016, mr.saffari@xxxxxxxxx [EnergyPlus_Support] wrote:


Hi all,

Anybody has experience of using EMS to make a unified output of PTHP electricity power ? I encounter errors when I use it!!!  I used the Average zone temperature of the whole building example but it does not work. For example in a 3-zone building I want to do this :


Whole PTHP power = PTHP power zone1 + PTHP power zone2 + PTHP power zone3


When to call the program ? before zone/HVAC reporting ?

What timestep should be used ?  System/Zone?


Kind regards,


 




__._,_.___

Posted by: Linda Lawrie <linda@xxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___