|
I am answering my own question. I didn’t look at the two files in enough detail.
The
v1.4_7.2_5 file has been updated to version 7.2. I did a file compare and found the differences between the two files. My apologies for not doing a thorough investigation before sending my query. Christopher Jones,
P.Eng.
WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Hello, I am hoping someone can provide some insight on this issue. I downloaded the DOE Commercial Reference Building Post 1980 models for Hospital � v1.4_7-2.zip When I open the Chicago .idf file, the version is listed as: ! Version 1.3_5.0
! EnergyPlus Version 5.0 The file name is
RefBldgHospitalPost1980_v1.4_7.2_5A_USA_IL_CHICAGO-OHARE.idf Did the file get updated but the comment not changed? I am wondering which version of EnergyPlus to use for running this file? Thanks! Christopher Jones,
P.Eng. WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Hi Christopher, I totally agree with you. Best, Sean Sean, You are correct, the secondary
pump can be either variable speed drive or one speed riding the curve. Riding the curve implies that the loop is variable flow (2-way valves on the coils). At least that is how I have always interpreted G3.3.3.10. Christopher Jones,
P.Eng. WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Hi Christopher, Thanks for your reply. But I think the chilled water secondary pump can be either variable flow (variable speed drive) or constant flow (however pump ride the pump curve) depending on the cooling capacity. Is it right? Best regards, Sean
Keep in mind that the chilled water secondary loop is variable flow regardless of the size of chiller.
Christopher Jones,
P.Eng. WSP Canada Inc. 2300 Yonge Street, Suite 2300 Toronto, ON M4P 1E4 F +1 416-487-9766 C +1 416-697-0056 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sean, After thinking about it, I think you're right, and the HVACTemplate from E+ is misleading.
References:
Code reference:
Best, Julien
-- 2016-02-22 12:12 GMT+01:00
seanking.1970@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
Hi Julien,
Thank you very much for your useful inputs.
However, when checking LEED table 1.4 form, it looks the case is different for boilers and chillers, there should be one HW pump even if two boilers are required (the hot water loop must be primary only), while one pump for each chiller shall be required together
with one pump each at condenser side (CW pump). And for Chilled Water Loop they do require primary-secondary setting so the primary subloop should use constant pump(s).
Is above observation right?
Thanks a lot.
Sean
G3.1.3.5 is pretty clear on that
So, just one pump (put it just after the supply side inlet or just before the supply side outlet), either constant or variable.
By the way for chillers, when they say (G3.1.3.10) that if you have 300 tons or more you need a primary secondary pumping system... That doesn't mean you should put one pump per chiller, and then one pump on the supply side. What it means is that you should
have a constant speed pump on the supply side (typically right after the supply inlet node) and one variable speed pump on the demand side, typically right after the demand side supply inlet node. If you use the HVACTemplate:ChillerWaterLoop and select ConstantPrimaryVariableSecondaryas
pumping configuration, that's what you get...See attached
--
2016-02-18 12:09 GMT+01:00 seanking.1970@... [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP’s electronic communications policy, please consult our Anti-Spam Commitment www.wspgroup.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to us at caslcompliance@xxxxxxxxxxxx so that we can promptly address your request. This message is intended only for the use of the individual or entity to which it is addressed, and may contain information which is privileged, confidential, proprietary or exempt from disclosure under applicable law. If you are not the intended recipient or the person responsible for delivering the message to the intended recipient, you are strictly prohibited from disclosing, distributing, copying or in any way using this message. If you have received this communication in error, please notify the sender, and destroy and delete any copies you may have received. WSP provides professional land surveying services through the following entities: WSP Surveys (AB) Limited Partnership and WSP Surveys (BC) Limited Partnership __._,_.___ Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |
Email file not found: C:\Users\lklawrie\Downloads\Embedded\image001319.png