Check for misplaced comma. Look in the idd file for the correct number of fields and inputs for the object.
On 3 Mar 2016 10:38 am, "Sajal Chowdhury
sajal_c@xxxxxxxxx [EnergyPlus_Support]" <
EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
Thank you Mr. Sharma. I already did the procedure but this time it showed Crash file and not run the engine. I have attached my idf. file ..if any solution come from anybody for Natural Cross Ventilation.Thank you.
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.
First thing would look at is 'AirflowNetwork Control' field in 'AirflowNetwork:SimulationControl' object. Is it set to 'NoMultizoneOrDistribution'? Try setting it to 'MultizoneWithoutDistribution' to see if it works.
On Wed, Mar 2, 2016 at 5:40 PM, Sajal Chowdhury
sajal_c@xxxxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
Recently I am doing Natural Cross Ventilation Simulation.
I input:
Room Air Model Type= cross ventilation
Room Air Setting=Cross Ventilation (Recirculation)
Zone Air flow > Zone Ventilation Design Flow Rate.
but the following errors ...
****Program Version,EnergyPlus-Windows-64 8.1.0.009, YMD=2016.03.02 21:10,IDD_Version 8.1.0.009
** Severe ** Problem with RoomAirSettings:CrossVentilation = Z-1
** ~~~ ** AirflowNetwork airflow model must be active in this zone
** Fatal ** GetAirModelData: Errors found getting air model input. Program terminates.
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=Problem with RoomAirSettings:CrossVentilation = Z-1
Please help to inform the proper steps.
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.
--
Chandan Sharma
Principal, Convergent Solutions