Careful what you measured.  I have modeled radiant heat systems when trying to mitigate potential condensation on surfaces.  What I found in E+ is that with the same air temperatures for control, radiant heat uses more energy than an air heat system.  This makes sense when you consider that a hot surfaces radiates more energy to cold surfaces and that comfort provided by radiant systems generally allows lower air temperature as a compensation.

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, March 04, 2016 8:09 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Not treated airflow

 

 

Thank you for your prompt answer. 

 

I have modeled a room equipped with a hydronic ceiling radiant system and the convective heat transfer coefficient results in a quite low value compared with the experimental results data (the average value is 1.55 in the model vs the value 3/4.5 W/m2K of the experiments). That’s why I had the idea to study the effect of a higher air recirculation. 

 

Mirko



__._,_.___

Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___