[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: DX coils consistency with ASHRAE 9.1-2007 Tab6.8.1A for a Baseline VAV system 5 with reheat





Definitely use 773.3 w / m3. That's the value used in the AHRI standard which is the reference for calculating Rated COP / EER. (It's also the default value in E+)

On Sat, Apr 16, 2016 at 7:43 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Let me start by saying that "the deeper you dig, the deeper the rabbit hole will go". The true answer and understanding of your questions are at a level Jim Dirks has well described as "black belt level". I'm not going to start explaining it all.

According to me, and there are other opinions out there, the most responsible way is to use the data derived curves of a equipment in the e+ database available to you. Choose the equipment (curves) that most closely match yours for type and full load capacity. Then adjust the rated fan power to the required value. Then adjust the rated gross COP until the reported net COP matches the requirement. The part-value requirement like IPLV or SEER will not match. If the baseline equipment is better than the minimum requirement, then it is conservative and you should be okay with the reviewer.

 

Thank you Jean for the reply.

That is what I suspected. About this this I have one or two more doubt.
I can't figure how to calculate the gross COP to make the standard rated net cop to be consistent with ashrae limitations.

The easiest way is to set up a parametric analisys to find the correct net COP varing the gross COP, but I found that also   !- Rated Evaporator Fan Power Per Volume Flow Rate {W/(m3/s)} set at the default 773.3 has an effect on net COP as well as on SEER and IEER.
The I/O ref seems to suggest only to change the 773.3 to obtain pvorrect values for SEER and IEER. In this way the parametric analisys shoul be performed with 2 parameters.

In my opinion this should not be the best way to solve the problem because it implies a sort of "blindness".
Looking for an help I found some examples on ASHRAE 90.1 user manual (examples  11-C and G-G) in which there are showed the calculation which involves the net and gross COP. Even if I found that the same calculations can be repeated using data reported in the html file ans obtaining analitically in this way net or gross cop, those calcs are performed not using user input from the idf.

I don't know if I have been clear in the previous description, but my question is this... in which way should I set the gross cop? Which approach should I follow? In which way should I manage the input   !- Rated Evaporator Fan Power Per Volume Flow Rate? Must I satisfy the consistency of IEER an SEER?

Thanks




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Guitar strings are in constant tension against the guitar's neck during their entire life. The tension doesnâ??t discourage the guitarâ??s neck. Rather, it allows beautiful music to be made. May it be so with our lives and their tensions.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___