Re: [EnergyPlus_Support] Setpoint manger control for a BASELINE system-6 (packaged rooftop VAV with reheat)





That seems like the right approach to take.

For G3.1.3.12, OA reset setpoint manager can be used to place these two cooling setpoints at AHU supply outlet

Setpoint at Outdoor High Temp: thermostat cooling setpoint - 11.1 C = 8.9 
Setpoint at Outdoor Low Temp: (thermostat cooling setpoint - 11.1 C) + 2.78 C = 11.68

If the zone requires heating, terminal reheat will reheat the air to (thermostat heating setpoint + 11.11) = 31.1

sizing:zone should use keyword "TemperatureDifference" and specify 11.1 as supply air temperature difference as you mentioned.

Other than OA reset, maybe mixed air setpoint manager is needed to take into account any
downstream system fan heat i.e. no warmest setpoint manager is needed.

On Thu, Apr 28, 2016 at 2:19 PM, telemar87@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Dear all,

I would like to know which type of setpoint manager should be set for the central AHU, if a baseline system-6 is being modelled.
ASHRAE 90.1 does not point particular configuration except @ G3.1.3.12 Supply air temperature reset: the air temperature for cooling shall be resethigher by 2.3°C (ASHRAE SI version).

I have some doubts about the setpoint manager that should be used.
The pre-built system-6 scheme proposed by DB uses an outdoor air reset in which actually a linear modulation in a 2.78°C band large is used. (2.78°C seems to be simply the conversion of the 5°F IP ASHRAE to °C, let's consider 2.3°C).

In my case the zones setpoint are 20°C in heating and 26°C in cooling (it's a multizone system). 
The zone heating equipment is dimensioned  for a temperature difference of 11°C, (in sizing:zone for heating and cooling is set a temperature difference of 11°C).
in this case the PIU outlet air temperature should be 31°C in heating and 15°C in cooling.

At this point, how the setpoint manager just after the AHU should be set? Which type of SPm should be used?
Intuitively I would use a warmest setpoint manager with a temperature set with 15°C minimum setpoint temperature and 17.3°C maximum setpoint temperature.

Is this approach correct? What do you usually do in this case?

Thanks,
Marco


 





--
Chandan Sharma
Principal, Convergent Solutions


__._,_.___

Posted by: Chandan Sharma <chandangsharma@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___