Julian is correct. Some third party GUIs do this for you so that you can input psi-values. They then use the linear thermal bridging values to either
1) derate the construction u-values by decreasing the insulation layer untill the equivalent u-value for the assembly is reached, or
2) they create a subsurface on the base surface with increased u-value to achieve the same equivalent area-weighted u-value for the assembly.

The second method may be a better indicator for condensation analysis on "cold spots" but is still not as good as using a FEM method (like from THERM).

The more surfaces your model has, the more computation time you will need, so the first method is better for speed.

Hope this helps,

Jean

On 23 May 2016 12:31 pm, "gauravciitr@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi,

What objects do we have to design thermal bridge in a building? Where can I put value of phi?


Thanks

Gaurav



__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___