Re: [EnergyPlus_Support] air cooler and ceiling fan





This type of ceiling fan doesn't bring outside air. It will have three effects in real life:
* Internal gains from the motor: In e+ you can add an electricequipment for that
* Increase air velocity leading to better PMV/PDD: you may increase air velocity by creating your own Air Velocity Schedule in the IDF file if you care about comfort
* De-stratify the air: by default E+ assumes a "fully mixed" room model, meaning the temperature is the same throughout the zone, so that won't be captured unless you want to use a more complex room model. I don't advise doing that since you seem to be a beginner.



--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr


2016-06-09 12:00 GMT+02:00 'balsam a. shalal' balsam.shalal@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Hi Julien,,
i highly appreciate your advice, but please what about the useing of ceiling fans???
I attached its photo, I hope you could give me some helpful data about it.
thanks in advance
Balsam




On Thursday, 9 June 2016, 8:49, "Julien Marrec julien.marrec@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:


 

--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr


2016-06-09 9:40 GMT+02:00 Julien MARREC julien.marrec@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 
Hi,

That's called an evaporative (or adiabatic) cooler. I can't recall if there's also a zonehvac component that does that but there's definitely a few that are air loop components (research special and cellpak). Look in the I/O reference guide for "evaporative"

Julien

Envoyé de mon iPhone

Le 9 juin 2016 à 00:43, "balsam.shalal@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :

 
Hi all,,,,
I hope somebody can help me with my questions, I use specific air cooler and ceiling fans for ventilation and cooling but  I couldn't find any information about these equipment in E+... I attached  a photo for this air cooler perhaps it could be  helpful to know if its specifications exist in E+ or not ???? I would appreciate any help
thanks in advance
<CC_Guideline_50.bmp>






__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___