Sajal,
It is almost impossible to say that everything is identical between the simulations because you are using different technology for your condensers.  Each of those three options has very different part load performance! 

In the case of the water and evaporatively-cooled condensers, the climate (specifically the humidity pattern) file will also have a big effect.

Part load performance is a complex topic which requires some extra study. If you want to compare specific equipment (i.e., specific manufacturer and model), then you need to obtain the part load performance values for the exact equipment. If you are conducting a generalized comparison and you have used default curves values for part-load performance, then you probably see big influence on efficiency / power as outdoor humidity varies.  The "winner" may vary in a dry climate compared to a humid climate. I'm guessing that you have used a fairly dry climate because the water-cooled system is the current "winner".

One more factor to consider is the water consumption and maintenance. I live in a place that has plentiful fresh water with fairly low cost, but that's not true everywhere. In addition, water-cooled systems generally require more maintenance and thus have higher life cycle costs than air-cooled systems.

On Thu, Jul 7, 2016 at 12:17 AM, Sajal Chowdhury sajal_c@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Dear All,
I have simulated HVAC: PTHP+Fan-Coil with chilled water loop and plant : chiller. I used 3 types of condenser i. water cooled, ii. evaporatively cooled and iii. air cooled. I found in all situations water cooled condenser type gave low cooling energy/electricity in all case than others condenser type. Can anybody help me to discuss why this happen and whats the logic? It may be noted here that the others conditions and parameters are same for the both simulations. Thank you and waiting for the discussion. 
 
Sajal Chowdhury
B.Arch.(BUET), M.Arch.(BUET), M.Eng.(HU,Japan)C.




--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

For breaking the natural law, there are natural penalties:
Those who live by knives die by them. Those who betray their friends lose them. Those who abandon their children never know the sweetness of their kiss. Those who travel from bed to bed lose the capacity for trust. Those who torture their consciences are tortured by them in return. Those who refuse the one in whose Image they are made live as strangers to themselves.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___