[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] FindRootSimpleController Sever errors





One of idf model I am working is showing me the Controller error as bellow for all the VAV Cooling coil controller


** Severe  ** FindRootSimpleController: Controller error for controller = "VAV_1_COOLC_CONTROLLER"

   **   ~~~   **  Environment=ANNUAL, at Simulation time=01/27 18:40 - 18:50

   **   ~~~   **   Controller function is inconsistent with user specified controller action = "" action

   **   ~~~   **   Actuator will be set to maximum action

   **   ~~~   ** Controller control type=Temperature

   **   ~~~   ** Controller temperature setpoint = 12.40 [C]

   **   ~~~   ** Controller sensed temperature = 16.65 [C]

   **   ~~~   ** Controller actuator mass flow rate set to 10.87 [kg/s]

   **   ~~~   ** Controller actuator temperature = 16.67 [C]

   **   ~~~   **   Note: Chilled water coils should be reverse action and the entering chilled

   **   ~~~   **         water temperature (controller actuator temperature) should be below the setpoint temperature

   **   ~~~   **   Note: Hot water coils should be normal action and the entering hot

   **   ~~~   **         water temperature (controller actuator temperature) should be above the setpoint temperature


I have set the ChilledWater coils to reverse action and my Controller is using setpointmanager as


SetpointManager:MixedAir,

    VAV_1_CoolC SAT Manager, !- Name

    Temperature,             !- Control Variable

    VAV_1 Supply Equipment Outlet Node,  !- Reference Setpoint Node Name

    VAV_1_HeatC-VAV_1_FanNode,  !- Fan Inlet Node Name

    VAV_1 Supply Equipment Outlet Node,  !- Fan Outlet Node Name

    VAV_1_CoolC-VAV_1_HeatCNode;  !- Setpoint Node or NodeList Name


*************  ** Severe  ** FindRootSimpleController: Previous controller action error continues for controller = VAV_1_COOLC_CONTROLLER

   *************  **   ~~~   **   This error occurred 11 total times;

   *************  **   ~~~   **   during Warmup 0 times;

  &nb

__._,_.___

Posted by: rajeevkamal@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___