[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] FindRootSimpleController Sever errors





I reported a similar issue to the helpdesk in 2013.  This was their response:

"The fix is to change all of your controller "Minimum Actuated Flow" fields to 0.0 and this file will run to completion. Non-zero min flow rates are not well supported and can cause issues. I generally set those to zero (everywhere they are available). That said, this should not cause a fatal error - we will try to sort that out "

What version of EnergyPlus are you using?  This may have been fixed.

--
Karen 

On Mon, Jul 11, 2016 at 12:34 PM rajeevkamal@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

One of idf model I am working is showing me the Controller error as bellow for all the VAV Cooling coil controller


** Severe  ** FindRootSimpleController: Controller error for controller = "VAV_1_COOLC_CONTROLLER"

   **   ~~~   **  Environment=ANNUAL, at Simulation time=01/27 18:40 - 18:50

   **   ~~~   **   Controller function is inconsistent with user specified controller action = "" action

   **   ~~~   **   Actuator will be set to maximum action

   **   ~~~   ** Controller control type=Temperature

   **   ~~~   ** Controller temperature setpoint = 12.40 [C]

   **   ~~~   ** Controller sensed temperature = 16.65 [C]

   **   ~~~   ** Controller actuator mass flow rate set to 10.87 [kg/s]

   **   ~~~   ** Controller actuator temperature = 16.67 [C]

   **   ~~~   **   Note: Chilled water coils should be reverse action and the entering chilled

   **   ~~~   **         water temperature (controller actuator temperature) should be below the setpoint temperature

   **   ~~~   **   Note: Hot water coils should be normal action and the entering hot

   **   ~~~   **         water temperature (controller actuator temperature) should be above the setpoint temperature


I have set the ChilledWater coils to reverse action and my Controller is using setpointmanager as


SetpointManager:MixedAir,

    VAV_1_CoolC SAT Manager, !- Name

    Temperature,             !- Control Variable

    VAV_1 Supply Equipment Outlet Node,  !- Reference Setpoint Node Name

    VAV_1_HeatC-VAV_1_FanNode,  !- Fan Inlet Node Name

    VAV_1 Supply Equipment Outlet Node,  !- Fan Outlet Node Name

    VAV_1_CoolC-VAV_1_HeatCNode;  !- Setpoint Node or NodeList Name


*************  ** Severe  ** FindRootSimpleController: Previous controller action error continues for controller = VAV_1_COOLC_CONTROLLER

   *************  **   ~~~   **   This error occurred 11 total times;

   *************  **   ~~~   **   during Warmup 0 times;

   *************  **   ~~~   **   during Sizing 0 times.


I get 48 of these warnings with year of simulation. Can this be ignored safely considering only 12 times in a year for each controller.




__._,_.___

Posted by: Karen Walkerman <kwalkerman@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___