Re: [EnergyPlus_Support] Re: Detailed Ice Storage system warning





Dear Rajeev, 

It did work to allow the Ice detailed object to converge with a PCM replacement for water ice. By working I mean that it did not have the warning and from memory the results where a bit better.  

How I did it was perhaps more complicated than most users would care to do- I modified the FORTRAN code in Energy Plus 8.1.009 and compiled the changes into a custom version.  I suppose this could be done in Energy Plus 8.5 C++ as well.  
My opinion is that the object should have an IDD field for max iterations rather than the Max iteration number declaration of 100. It seems to me that the developer of this module must have tested it with water ice that melts at 0C rather than a PCM that melts at another temperature. 

Inline image 1 









Jeremiah Crossett | Chief Technological Officer | NRGsim Inc. 
7409 SW Capitol Highway Portland OR, 97219 #204
503-688-8951 | www.nrgsim.com

On Thu, Jul 14, 2016 at 11:51 AM, rajeevkamal@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Jeremiah,


Did changing the iteration from 100 to 1000 solved the problem for you? If so, how did you change it? I am getting similar warnings in my Ice tank simulation

  *************  ** Warning ** Detailed Ice Storage system [TES TANK]  discharging maximum iteration limit exceeded occurrence continues.
   *************  **   ~~~   **   This error occurred 39906 total times;
   *************  **   ~~~   **   during Warmup 0 times;
   *************  **   ~~~   **   during Sizing 0 times.


Rajeev




__._,_.___

Posted by: Jeremiah Crossett <jcrossett@xxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___