Are you referring to the tables in the eplusout.html for site/source energy? In which case that is the *electricity* consumption used by a heat rejection device such as a cooling tower or fluid (dry) cooler. In the case of a cooling tower that's mostly to run the fan (and potentially the basin heater for water operation), most of the work is done by water evaporation so logically it will appear small on a kWh (or BTU) basis. If you think about a one room model cooled by water cooler chiller and cooling tower: the cooling load is the amount of energy that needs to be removed From the room to get the required temperature setpoint. The chiller will work to do so and consume electricity (much less, since the COP of the chiller is typically between 4-10. Then the cooling tower has to disperse this heat load + the chiller's compressor heat (and some pump heat load too) and will consume both electricity and water. Hope that overly simplified explanation is helpful Julien Envoyé de mon iPhone Le 2 oct. 2016 à 12:49, "keivan bamdad keivan.bamdad@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien MARREC <julien.marrec@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |