Re: [EnergyPlus_Support] Heat Rejection Meaning





Correctly explained by Julien. 
Q_condenser=Q_cooling_duty+W_compressor

So cooling tower is handling the Q_condenser (rejected). But you said "heat that cooling tower rejects to the atmosphere is a lot, so why its value is very small". 

Are you sure you get Q_rejected < Q_cooling_duty?

Tilek

On Sun, Oct 2, 2016 at 9:49 PM, keivan bamdad keivan.bamdad@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi folks,
Does anyone know what heat rejection is? It is said that it is for Cooling Tower, but the amount of heat that cooling tower rejects to the atmosphere is a lot, so why its value is very small in the output of EnergyPlus? what is the difference between heat rejection and cooling loads? 

I highly appreciate your response.

Best regards,
Kev




--
Tilek Aberra,
12 Bainton Pl., Doonside,
Sydney, Australia
ph:   +61 (0)2 9534 4731 (home)
         +61 (0)2 8805 0421 (office)
mo:  +61 (0)4 3959 5937


__._,_.___

Posted by: Tilek Aberra <tilek.aberra@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___