[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model





Hi,
Thanks for the reply. Can you please suggest me good resource to learn air flow network
method? I am reading InputOutputReference document. I will really appreciate. 



From: "allinson_louis@xxxxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thursday, December 8, 2016 3:56 PM
Subject: [EnergyPlus_Support] Re: Need help for Naturally Ventilated Model

 
Hi

No you cannot assume 3 ACH. Natural ventilation airflow is dependent on buoyancy driven (caused by internal/external temperature difference) and wind driven. These vary transiently and therefore you will not be delivering a constant ventilation rate, even if you are controlling the vent.

ideally you want to use the airflow network to model airlfow through the windows. You also want to then control the window openings such that you deliver the necessary airflow for IAQ (CIBSE guide B recommends 10l/s/person) when occupied and the sufficient airflow to mitigate overheating.

i suggest that you read section Group - airflow network in the inputoutput document

you could also use an interface like DesignBuilder and read their help files on modelling ventilation through a window


kind regards







__._,_.___

Posted by: bhavana patil <ana5patil@xxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___