[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Need help for ExternalInterface:Actuator





Yes, I was a little too quick to answer, the correct syntaxis is :

ExternalInterface:Actuator,

    Block1_Zone1_HVAC,   !- Name

    Block1:Zone1:HVAC,   !- Actuated Component Unique Name

    Ideal Loads Air System,       !- Actuated Component Type

    Air Mass Flow Rate,           !- Actuated Component Control Type

     ;   !- Initial Value


I test this way and it is working.

By the way, your are not given the correct information from the err file; the message "Preceding condition causes termination." means that you have something writen before than showing you the problem:

   ** Severe  ** Invalid Actuated Component Type =xxx
   **   ~~~   ** Entered in EnergyManagementSystem:Actuator=BLOCK1_ZONE1_HVAC
   **   ~~~   ** Component Type not found
   **   ~~~   ** Review .edd file for valid component types.

if you read correctly this message, you can see than the .edd file can help you with actuators... See the manual for using edd file.


__._,_.___

Posted by: f.simon.mail@xxxxxxxxx


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___