|
Hi, I could be wrong but I don't think there's an option to do this right out of the box in E+ (meaning there isn't a field to add an exhaust air node at the condenser air inlet node but that's easy to check). Otherwise you can do this with EnergyManagementSystem (EMS). The logic would likely be similar to this: Put a sensor for temperature (and flow rate) at the exhaust air node of your airloopHVAC(s), and an actuator or the outdoor air node for the condenser inlet and overwrite its temperature via an EMS program. You'll likely need to do some calculation on the temperature if you think your exhaust airflow is lower than the condenser inlet airflow needed (in this case a sensor for the flow rate is needed too). Hope that helps, Julien Envoyé de mon iPhone Le 16 janv. 2017 à 00:06, "tilek.aberra@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx> a écrit :
__._,_.___ Posted by: Julien MARREC <julien.marrec@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |