Hi Julien,

I mostly use E+ for the refrigeration system module, and for the air condensers of some of the refrigeration systems there is the option to use an air exhaust node (for Air Inlet Node Name), otherwise the default node (if left blank) for condensers inlet is the outside DB. As follows for instance:

Refrigeration:GasCooler:AirCooled,
    RefrigGasCooler,         !- Name
    GasCoolerHRCurve,        !- Rated Total Heat Rejection Rate Curve Name
    Fixed,                   !- Gas Cooler Fan Speed Control Type
    8000.0,                  !- Rated Fan Power {W}
    0.2,                     !- Minimum Fan Air Flow Ratio {dimensionless}
    27.0,                    !- Transition Temperature {C}
    3.0,                     !- Transcritical Approach Temperature {DeltaC}
    10.0,                    !- Subcritical Temperature Difference {DeltaC}
    10.0,                    !- Minimum Condensing Temperature {C}
    ,                        !- Air Inlet Node Name
    RefrigGasCooler;         !- End-Use Subcategory

And you said use EMS; I am ok to do that, but which one is "exhaust air node of your airloopHVAC" for the ExampleFile I referred. The only ExampleFiles I saw where the "exhaust air node" is explicitly defined is for those with "AirflowNetwork". I never looked at the use of "AirflowNetwork" before, and also did not want to spend on this new application if it would easily be figured out with simpler simulations. Anyway thanks for your input.

I will do a further assessment if I need to spend more time on this versus the potential energy reclaim/benefit.

Regards,

TA

On Tue, Jan 17, 2017 at 9:16 PM, Julien MARREC julien.marrec@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Hi,

I could be wrong but I don't think there's an option to do this right out of the box in E+ (meaning there isn't a field to add an exhaust air node at the condenser air inlet node but that's easy to check).

Otherwise you can do this with EnergyManagementSystem (EMS). The logic would likely be similar to this:
Put a sensor for temperature (and flow rate) at the exhaust air node of your airloopHVAC(s), and an actuator or the outdoor air node for the condenser inlet and overwrite its temperature via an EMS program. You'll likely need to do some calculation on the temperature if you think your exhaust airflow is lower than the condenser inlet airflow needed (in this case a sensor for the flow rate is needed too).

Hope that helps,
Julien 

Envoyé de mon iPhone

Le 16 janv. 2017 à 00:06, "tilek.aberra@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@yahoogroups.com> a écrit :

 

Hi,

How do I extract the exhaust air temperature and flow rate of an air conditioned building from an Energyplus simulation? I was thinking to reclaim some of the cooling in the exhaust air for condenser cooling. Can someone guide me on this using one from the ExampleFiles, say "5ZoneAirCooled.idf" or share me their experience.


Regards,

Tilek

 




--
Tilek Aberra,
12 Bainton Pl., Doonside,
Sydney, Australia
ph:   +61 (0)2 9534 4731 (home)
         +61 (0)2 8805 0421 (office)
mo:  +61 (0)4 3959 5937


__._,_.___

Posted by: Tilek Aberra <tilek.aberra@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___