... and some materials, like polyisocyanurate, change U value as they age.

On Wed, Jan 18, 2017 at 11:02 AM, Jean Marais jeannieboef@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

Joe and Edd have good points, however for most estimates we assume the effect is negligable for the "surface to surface" U-value. What does change are the film resistances which are convection dependant...and e+ calculates those dynamically. So the overall u-values are changing all the time. This is not to be confused with RATED u-values, which are the manufacturer specs at given rating test conditions.

2017-01-18 15:56 GMT+01:00 'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@yahoogroups.com>:
 

A lot of that work is now part of the WUFI program.  WUFI materials can have variable R-Values with temperature and moisture content and WUFI will calculate instantaneous total assembly R-Values.  This is a likely coming standard that will need to be integrated into E+.

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files

From: EnergyPlus_Support@yahoogroups.com [mailto:EnergyPlus_Support@yahoogroups.com]
Sent: Wednesday, January 18, 2017 12:05 AM
To: EnergyPlus_Support@yahoogroups.com
Subject: Re: [EnergyPlus_Support] Does U-value change with temperature?

 

 

I remember seeing a report by Jeff Christian of ORNL decades ago that looked into the change in conductivity for insulation products as a function of temperature.  I recall he found something like a 10% change over the range of ambient temperatures.  If you're interested, you should do a Google Search of the technical literature (or ORNL reports) and see if you find something.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang@whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"

On 1/11/2017 10:42 PM, Amrita Ghosh amritaghosh1986@xxxxxxxxx [EnergyPlus_Support] wrote:

 

Hi,

 

Can anyone tell me if U-value of a material changes with temperature? 

 

While evaluating the U-value, if the convective heat transfer coefficients (h) change, the U-value changes. But does it also change when the temperature, indoor or outdoor, changes? Since the equation states: U=Q/(A. deltaT)

where deltaT= temperature difference between indoor and outdoor.

 

Thank you,

Amrita

 





--

James V Dirkes II, PE, BEMP, LEED AP
CEO/President
The Building Performance Team Inc.
1631 Acacia Dr, GR, Mi 49504

Direct: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn | May 2016 ASHRAE Journal article on energy modeling

...and the more I considered Christianity, the more I found that while it had established a rule and order, the chief aim of that order was to give room for good things to run wild.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___