Re: [EnergyPlus_Support] PlantLoop, Boiler and outdoor air temperature reset control



Thank you Chandan, that is a great tip.

Quoting "Chandan Sharma chandangsharma@xxxxxxxxx [EnergyPlus_Support]"  
<EnergyPlus_Support@xxxxxxxxxxxxxxx>:

> EnergyPlus example file which has OutdoorAirTemperatureReset in
> HVACTemplate object when run with EP-Launch utility will produce expanded
> *.expidf file. This will show how OA reset is done in detailed plant loop.
> Basically SetpointManager:OutdoorAirReset will have to be added in the
> detailed plant loop.
>
> On Wed, Feb 8, 2017 at 9:54 PM, Chris Jones cj@xxxxxxxxxxx
> [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
>
>>
>>
>>
>>
>> Hello,
>> I am hoping to apply a boiler supply temperature reset control based
>> on outdoor air temperature. I am using PlantLoop and not
>> HVACTemplate:Plant:HotWaterLoop.
>>
>> The Input-Output reference provides documentation for applying the
>> OutdoorAirTemperatureReset hot water setpoint reset type when using
>> HVACTemplate:Plant:HotWaterLoop.
>>
>> Hopefully there is a way to use this type of control with PlantLoop
>> and Boiler:HotWater?
>>
>> Thank you for any assistance!
>> --
>>
>> Chris Jones
>> 14 Oneida Avenue
>> Toronto, ON M5J 2E3
>> 416-697-0056 <(416)%20697-0056>
>>
>>
>>
>
>
>
> --
> Chandan Sharma
> Principal, Convergent Solutions
> LinkedIn <https://in.linkedin.com/in/chandangsharma%E2%80%8B> | Website
> <http://convergentsolutions.co.in/>


-- 

Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3
416-697-0056



------------------------------------
Posted by: Chris Jones <cj@xxxxxxxxxxx>
------------------------------------

EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.
------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/