I found the spreadsheet used to create that performance curve. Use 
Entering water temperature. Note cells BJ12 - BJ119 use 30C and 60C as 
the return water temperature to yield the regression coefficients in 
AX112-AX117 which match the Boilers.idf performance curve.

On 2/9/2017 10:43 AM, Chris Jones cj@xxxxxxxxxxx [EnergyPlus_Support] wrote:
> The EnergyPlus installation includes the Boilers.idf file in the
> Datasets directory. This file includes a Biquadratic, condensing
> boiler curve. What isnâ??t clear is if this curve is based on the boiler
> Entering or Leaving temperature.
>
> The reference for this curve is from Viessmann and all the Viessmann
> condensing boiler literature I have reviewed states the boiler
> efficiency is dependent on system heating water return temperature.
>
> Should I specify Entering or Leaving when using this curve?
>
> Thanks for your assistance!

-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/

Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/


<*> View Attachments on Web https://groups.yahoo.com/neo/groups/EnergyPlus_Support/attachments/1630917568;_ylc=X3oDMTJxZGtwNWVxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNhdHRhY2htZW50BHNsawN2aWV3T25XZWIEc3RpbWUDMTQ4NjY2MDM2Mg--
------------------------------------
Posted by: Richard Raustad <rraustad@xxxxxxxxxxxx>
------------------------------------

EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.
------------------------------------

Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    https://info.yahoo.com/legal/us/yahoo/utos/terms/
Attachment not found:
D:\Eudora\Attach\CondensingBoilerCurveFit.jpg