Dear Francesco,
try to check if the system is available for the zone "SPOGLIATOIO MASCHILE" or there are the conditions in order to turn on the system at the data time of peak.




----Messaggio originale----
Da: "fpasserini.tn@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Data: 11/05/2017 15.25
A: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Ogg: Re: [EnergyPlus_Support] Re: Calculated Design Load = 0 ? [1 Attachment]

 

The heating setpoint and the cooling setpoint are different. The cooling setpoint was imposed equal to 100°C in order to avoid that the room requires cooling.

I have attached a graph relative to the heating designday. You can see that "System Node Setpoint Temperature" seems equal to the highest temperature between the zone temperature and the thermostat heating temperature.
Although it has the same sizing parameters of the other zones, the zone 00:LocalePersonale doesn't even compare in the table "Zone Sensible Heating" of the html report!?
I get the following warnings:

   ** Warning ** Calculated design cooling load for zone=00:LOCALEPERSONALE is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
   ** Warning ** Calculated design heating load for zone=00:LOCALEPERSONALE is zero.
   **   ~~~   ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
 





__._,_.___

Posted by: "roberto.xs@xxxxxxxxx" <roberto.xs@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___