Thanks for your full explanation�I agree�my issue is that tt the inputs for a two speed D coil are not following the game plan.  Increasing SHR stops humidity calculation errors�

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER
781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, June 30, 2017 4:05 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Coil:Cooling:DX:TwoSpeed and SHR

 

 

Edward,

 

DX cooling coils that are running at lower speed, which also implies lower supply air flow rate, is expected to have lower SHR compared to higher speed. The main reason is that the whole coil surface area is available for lower supply air flow, hence a better coil surface and air contact that enhances moisture removal. When the air has more contact with the cold coil surface, the fraction of supply air approaching the apparatus dew point increases, which enhances de-humidification potential.

 

Some humidity control features of DX system allow the supply fan to run at reduced supply air flow rate to enhance de-humidification potential.     

 

Hope this helps, 

Bereket

 

 


From: "'Edward G. Lyon' eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
To: "'EnergyPlus_Support@xxxxxxxxxxxxxxx'" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Friday, June 30, 2017 3:18 PM
Subject: [EnergyPlus_Support] Coil:Cooling:DX:TwoSpeed and SHR

 

 

I am modeling an existing building with several roof top VAV systems.  I have system model numbers so I did not autosize any of the Coil:Cooling:DX:TwoSpeed system.  The SHR inputs for the model and error messages running the model make no sense to me:

 

Manufacturer data says SHR at low speed is much lower than at high speed (makes perfect sense to me), but E+ complains if the high speed and low speed SHR differ too much.

 

Using manufacturer data to calculate SHR inputs results in psychrometric calculation errors about RH exceeding 100%.  While the error message would suggest that more latent cooling is needed (lower SHR) the actual fix is to increase the SHR (less latent cooling).

 

So my model runs now runs without complaints with high speed SHR = low speed SHR = 0.77, not close to the manufacturer data. I would appreciate it if anyone could explain this E+ logic to me this.    

 

Ned Lyon, P.E. (MA, WV)
Staff Consultant

SIMPSON GUMPERTZ & HEGER 
     | Engineering of Structures and Building Enclosures

41 Seyon Street, Building 1, Suite 500
Waltham, MA 02453

781.907.9000 main
781.907.9350 direct 
617.285.2162 mobile 
781.907.9009 fax
www.sgh.com

Send Files

 



__._,_.___

Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___