I should know by now when I have to answer my own questions. Funny things happen when you have to make a two dimensional window frame flat for an E+ calculation. I have a typical thermally broken aluminum frame about 50mm
tall by 150mm wide for which THERM calculates a U-Value of about 7 w/m2-K. E+ wants a U-Value for something flat that is 50mm wide without air films. The THERM air films are 26 w/m2-K exterior and 3.29 w.m2-K interior for a total U-Value of 2.92 w/m2-K for
just conductive air films. (This means I could do better with no frame?) So there has to be a lot of radiant heat loss to boost the frame up to 7 w/m2-K heat loss calculated by THERM. Now what has to happen is the E+ frame conductivity has to be very large
(or black hole negative) and apparently it defaults to maximum of about 500 w/m2-K (no air films). Along the way with THERM/WINDOW we get center of glass U-Value and edge of glass U-Value. E+ now calculates center of glass internally. THERM gives us an edge
of glass U-Value from which a ratio of center to edge is calculated for E+. WINDOW also passes other glass properties along so E+ can internally calculate absorptions, reflections, and such. What is horribly confusing is if you use a standard thermally broken frame from the WINDOW library as a base line check, the U-Value passed to E+ is around 50
w/m2-K, and one would think a modern thermally broken frame could do a lot better. The WINDOW library frame is apparently an older ASHRAE calculation that probably should not be used at all any more. (And if you have a truly low, THERM U-Value for a frame,
WINDOW passes a value less than 500 w/m2-K to E+.) So the most important bottom line is that changing to high performance window frames does not impact the window frame heat loss calculations in E+ at all. The
only energy difference frames would make in E+ is if the frame area is reduced. The only other place some differences manifest themselves is in the edge of glass heat loss associated with a THERM calculated thermally improved frame. So now if you want to calculate a single glazed baseline to see the performance difference of films or multiple glass layers, you will hit another wall. All
the aluminum frame single glaze (and several other frame types) I have calculated loose heat from the frame to the edge of glass. This makes THERM calculate and edge of glass heat loss that is less than the center of glass heat loss, a no no by the imposed
rules of E+. The work around is to edit the THERM results imported to WINDOW to make the edge of glass equal to the center of glass and let the rest come out in the frame wash, but the one dimensional frame heat loss is probably questionable. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Okay, we're on the same page. The last time I was doing this was with v7.2. I was checking how to reverse engineer a window with European rating conditions so that WINDOW shows the correct results using EU ratings, switch to NFRC ratings
(check how much SHGC and U-values differ for interest sake) and then export the IDF code from WINDOW for e+. I checked values with a spreadsheet to follow if the edge of glass parameters were sane. Everything checked out okay. I had used Therm as a pre-process only if no values were available for the frame. Also then I didn't get crazy values. Something is going wrong in your THERM calculation. I would focus there. Am 02.11.2017 1:30 nachm. schrieb "'Edward G. Lyon'
eglyon@xxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
__._,_.___ Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |