Giacomo,
This is not what you asked, but I have never seen a chiller which operates in On / Off mode. Are you confident that is the scenario you want to model?

For example, some chillers use unloaders or other mechanical unloading means, while some use variable speed drives. The part load performance will differ for each of those, but that's not the same as on / off.

On Mon, Jan 29, 2018 at 4:05 AM, giacomo_luddeni@xxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I'm working on a project that consists in the evaluation of various chiller replacement options for a chilled water application. Among the different options, I need to model chillers with and without inverter (i.e. variable capacity and on/off operation).

I tried to compare the two operations. In the attached plot, you can see the same chiller (same nominal power, COP, mass flow rate, performance curves) operated in the on/off mode (minimum PLR and minimum unloading ratio set to 1, blue) and continuously (minimum PLR and Unloading ratio set to 0.2, red). I came up with the odd result that the on/off chiller is more convenient than the inverter regulated one. It seems to me that the cycling ratio is somehow equivalent to the PLR, in terms of how it scales down the available capacity to the actual demand, neglecting that, in fact, inverter regulation of the compressor motors allows to smoothly follow the load, avoiding peak startup current.

Did I interpret it correctly? Is there any way to make the model more consistent, taking into account the benefits of inverter regulation? Thanks





--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504

(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Coffee conversation: The first idea is the worst, but it is the most important because it starts discussion and becomes the building block for other ideas.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___