[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

RE: [EnergyPlus_Support] DOAS serving VAV compartment fans





That note is in the energy modeling report submission. The HVAC system is DOAS serving per floor VAV systems that in turn serve zone VAV boxes. Perhaps EnergyPlus cannot model this arrangement?

 

 

Christopher R. Jones, P.Eng.

Technical Specialist

Sustainability & Energy

 

T +1 416-644-0252

 

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4 Canada

wsp.com

 

 

Please consider the environment before printing...

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Thursday, February 01, 2018 10:26 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] DOAS serving VAV compartment fans

 

 

Most zone equipment can be connected to a DOAS system. Where are you seeing "EnergyPlus does not include the capability to model a DOAS providing outdoor air to another HVAC system"?

On 2/1/2018 9:36 AM, 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support] wrote:

I am reviewing an energy model submission done with EnergyPlus 8.7.. The energy modeling report notes that EnergyPlus does not include the capability to model a DOAS providing outdoor air to another HVAC system. I am not very well versed on the capabilities of EnergyPlus but this seens like a fairly significant shortcoming if it is in fact true?

 

 

 

Christopher R. Jones, P.Eng.

Technical Specialist

Sustainability & Energy

 

T +1 416-644-0252

 

2300 Yonge Street, Suite 2300

Toronto, ON M4P 1E4 Canada


wsp.com

 

 

Please consider the environment before printing...

 

 

 




NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited.. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance@xxxxxxx so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.

AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap@xxxxxxx afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.



-LAEmHhHzdJzBlTWfa4Hgs7pbKl



-- 
Richard Raustad
Florida Solar Energy Center
1679 Clearlake Road
Cocoa, FL 32922
Ph: (321)638-1454
http://www.fsec.ucf.edu/en/
 
Program Director
Electric Vehicle Transportation Center
http://evtc.fsec.ucf.edu/



__._,_.___

Posted by: "Jones, Christopher" <Christopher.r.Jones@xxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___