I think the problem lies in your input solar radiation, where the direct normal and diffuse horizontal are given as constant values for all sunlight hours: This is simply wrong. The diffuse horizontal should be the same
as the global horizontal minus the direct normal * sine (solar
angle). In your case, I see that the diffuse horizontal is higher
than the global horizontal for an hour at sunrise and for two
hours before sunset, which are impossible. Also, the (direct
normal)/sine (solar angle) cannot be larger than the global
horizontal. I haven't bothered to check that but I guess is
you've also violated that for a number of hours. If you're using
the EnergyPlus WeatherConverter to create the epw file, I'm
actually surprised that it did not catch conditions that are
outside of physical reality. A correct or more plausible (:-) ) clear sky profile should look something like this (Phoenix AZ average October day) : The current ASHRAE Clear Sky Model allows you to create such profiles for more than 5,000 locations around the world, so you should just use that to get a more realistic solar radiation profiles for your particular location. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 205A Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx http://weather.whiteboxtechnologies.com for simulation-ready weather data (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" On 2/7/2018 4:13 PM,
carlobianchi89@xxxxxxxxx [EnergyPlus_Support] wrote:
__._,_.___ Posted by: Joe Huang <yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |