[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] unable to reach set point temperatures in zones





The thing to understand with radiant systems is that the energy is transfered to the air node via convection from the surface area. Even the radiative energy will go to other surfaces and only effect the zone air if it is convected into the air. So there are exactly 3 variables which effect the capacity of the system:
1) area of radiant surface (m2)
2) convection coefficient (calculated by e+, as per the default or model selected)
3) Temperature of the surface
Check these and make sure the active surface is not turning off due to high humidity.

The sizing routine effectively exchanges energy directly with the air such as to keep the setpoint at all times and is not subject to the same "lag" as the radiant system. Make sure your design day set point curve is a flat line and that all internal loads associated with it are also a flat line. This gives a nice steady state peak. Then use the sizing factors to "oversize" the system to get the pull down times to about 30 min for an air system like a fancoil. A radiant system is mainly bound by active area. It doesn't matter if you have a super big pump, and ice cold water. Oversizing is useless if you are area limited.


__._,_.___

Posted by: Jean Marais <jeannieboef@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___