Please see the below attached file of radiant cooling system served by a purchase cooling.
I designed as per Design Day conditons and I got the cooling load for set point temperature of 24 degC ....
Purchased cooling Design capacity: 14.876 kW
Flow rate: 0.001772 m3/sec
when I simulated for the same city, I am not getting temepratures equal to that of set point.
These are the peak temperatures that I am noticing:
west Zone: 30.9572 degC
east Zone: 31.1degC
North zone: 28.67 degC
peak cooling capacity of Purchased cooling observed in simulation reports is : 35.2613 which is way higher than the design capacity 14.876 kW. Why is this? the peak capacity should not be greater than the design one right?
peak cooling zone capacities areÂ
west zone: 12.414 kW
East zone: 11.331kW
North Zone: 12.707kW
where as the design capacities areÂ
west zone: 4.454 kW
East zone: 4.575kW
North Zone: 5.846 kW
Why is this? the peak capacity should not be greater than the design one right?
during what conditions I can see both the simualted peak capacity and design capacity same?
What should I do to pull down the temperatures to that of set points? eventhough it is not practical, I maintained the temperature of cooling water as 5 degC. I tried changing the capacity of purchased cooling. but it is limted to accept only upto certain capacities. beyond that it is not accepting...what should I do to pull down the temperatures?
--Javed Iqbal, LEED AP, CEASr. Energy AnalystÂ
__._,_.___