[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Minimum Equipment Efficiencies- Non Standard conditions 6.8.1C





Dear All,

This is not a direct question regarding simulation or E+ tool but about the ASHREA 90.1-2010 minimum efficiency requirements to comply with 6.8.1C for the chillers at Non Standard Conditions.

We are working on a project where designer shared chiller efficiencies at design conditions whereas table 6.8.1C gives chiller efficiency at ARI conditions. In order to show compliance we have done Kadj calculation as prescribed under 6.4.1.2 to adjust ASHRAE 90.1-2010 baseline efficiency at design conditions. Now my doubt is

1. What value of baseline chiller efficiency to be used in simulation to compare the performance of the chiller with the Proposed/design case; direct COP value from table 6.8.1C OR COP after Kadj calculations?
2. Does anyone has copy of Addenda CH?

Thank you for your expert advice.

regards,

--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 







__._,_.___

Posted by: Javed Iqbal <eee.javed@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___