Re: [EnergyPlus_Support] water flow rate in primary and secondary loop





Francesco,
It's common for a primary pump to operate at constant speed whenever the chiller is operating. The pump should be OFF when the chiller is OFF.

The ASHRAE 90.1-specified pump power should be split between primary and secondary pumps (though ASHRAE does not specify the ratio)

On Sat, Aug 25, 2018 at 11:21 AM, fpasserini.tn@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

I am modeling System 7 with primary CHW loop and secondary CHW loop, according to ASHRAE 90.1-2007..

If I see the output, it seems that the primary water pump is always working, even when the secondary pump isnâ??t. Is that fine?

See attached images relative to the primary and to the secondary water flow rate.

Best Regards

Francesco





--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504

(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Coffee conversation:

You are hereby authorized to make two big mistakes each year, otherwise you will never learn anything.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___