You could lower the outdoor temperature in the design day object. Keep
in mind that it is OK to not reach the peak load on a few days of the
year so that the HVAC system does not need to be sized larger than
needed for most of the year. You can also look at the number of heating
hours not met to get an indication of how often this is a problem.
Meeting 95% of the load on the peak day sounds reasonable and only a few
10s or low 100s of heating hours not met also seems reasonable.
On 2018-08-31 14:34, my_sunny_night@xxxxxxxxx [EnergyPlus_Support]
wrote:
> Hello,
> I am using auto sizing for HVAC calculation using winter design day.
> However, the peak load across the whole year is higher than the peak
> load during design day.
> Any help would be appreciated.
>
>
>
> Links:
> ------
> [1]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlNnRiOWhlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUzNTc0MDQ1MQ--
> [2]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZmw5c3F1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MzU3NDA0NTE-
> [3]
> https://groups.yahoo.com/neo;_ylc=X3oDMTJkNGJpdnFwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTM1NzQwNDUx
> [4] https://info.yahoo.com/privacy/us/yahoo/groups/details.html
> [5] https://info.yahoo.com/legal/us/yahoo/utos/terms/
------------------------------------
Posted by: rraustad <rraustad@xxxxxxxxxxxx>
------------------------------------
EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The EnergyPlus web site is found at:
http://www.energyplus.net/
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
------------------------------------
Yahoo Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo Groups is subject to:
https://info.yahoo.com/legal/us/yahoo/utos/terms/