Re: [EnergyPlus_Support] Autosizing HVAC and peak load





Another way is to add a separate DesignDay object for each month. These are found in the same manner as opening an IDF, except you select the "DesignDay" file type (see lower right corner of the image.

This approach is more common for cooling loads which sometimes peak at a non-typical month, such as when glazing is a major factor and cause a peak cooling load in the winter months. (Thanks Mike Witte!), but it may help you.

I think Richard's suggestion will work well for you.



On Fri, Aug 31, 2018 at 3:25 PM, rraustad RRaustad@xxxxxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx> wrote:
 

You could lower the outdoor temperature in the design day object. Keep
in mind that it is OK to not reach the peak load on a few days of the
year so that the HVAC system does not need to be sized larger than
needed for most of the year. You can also look at the number of heating
hours not met to get an indication of how often this is a problem.
Meeting 95% of the load on the peak day sounds reasonable and only a few
10s or low 100s of heating hours not met also seems reasonable.

On 2018-08-31 14:34, my_sunny_night@xxxxxxxxx [EnergyPlus_Support]
wrote:
> Hello,
> I am using auto sizing for HVAC calculation using winter design day.
> However, the peak load across the whole year is higher than the peak
> load during design day.
> Any help would be appreciated.
>
>
>
> Links:
> ------
> [1]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlNnRiOWhlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUzNTc0MDQ1MQ--
> [2]
> https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZmw5c3F1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MzU3NDA0NTE-
> [3]
> https://groups.yahoo.com/neo;_ylc=X3oDMTJkNGJpdnFwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTM1NzQwNDUx
> [4] https://info.yahoo.com/privacy/us/yahoo/groups/details.html
> [5] https://info.yahoo.com/legal/us/yahoo/utos/terms/




--

James V Dirkes II, CEO / President
The Building Performance Team Inc.
1631 Acacia Dr, Grand Rapids, MI 49504

(alphabet soup of efforts for greater understanding: PE, BEMP, BCxP, LEED AP)

Direct / Mobile: 616.450.8653
jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx

Website l  LinkedIn

Coffee conversation:

You are hereby authorized to make two big mistakes each year, otherwise you will never learn anything.



__._,_.___

Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups..yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___