|
Christopher,
I'd suggest that the modeler use:
- for a multiple zone system: SetpointManager:MultiZone:MinimumHumidity:Average
- for a single zone system: SetpointManager:SingleZone:Humidity:Minimum
"Officially", E+ is not measuring humidity at the return air node, but it's doing effectively the same thing by determining the zone
return air humidity.
From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of 'Jones, Christopher' christopher.r.jones@xxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Friday, February 15, 2019 2:16 PM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject: [EnergyPlus_Support] EnergyPlus humidification control I am reviewing a LEED 2009 submission. The design sequence of operations calls for humidification to be controlled by measuring the return air stream RH. The modeler states that it is not possible for EnergyPlus v9.0 to model this control strategy. Is this the case? I am used to IES where it is possible with a few clicks.
Christopher R Jones, P.Eng. T+ 1 416-644-0252
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited.. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance@xxxxxxx so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages. AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap@xxxxxxx afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux. -LAEmHhHzdJzBlTWfa4Hgs7pbKl __._,_.___ Posted by: Jim Dirkes <Jim@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |