Ooi,
If you are considering a direct evaporative cooler:
If you are considering an INdirect evaporative cooler (which seems to be the case):
The effectiveness is always a fraction of the difference between the primary air's dry bulb and wet bulb temperatures. That product (eff x delta T) becomes the delta T of the secondary airstream.
James V Dirkes II, PE, BEMP, BCxP
Team Lead - Building Performance
616 450 8653
Foresight Management
Coffee Conversation:
If “freedom” is ability to do whatever we want, whenever we want and with whomever… that’s lawlessness or anarchy. Try that with traffic…. then think about what might happen if you try it with your life. From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx> on behalf of Ooi Koon Beng ooi_kb3@xxxxxxxxxxx [EnergyPlus_Support]
<EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Saturday, July 6, 2019 9:05 PM To: EnergyPlus_Support@xxxxxxxxxxxxxxx; energyPlus energyPlus Subject: [EnergyPlus_Support] Direct Evaporative Cooler - documentation
Dear all,
In the EngineeringReference, the formula for the saturation efficiency
does not seem to be correct
The InputOutputReference says that the Todb and Towb should be Tidb and Tiwb respectively
best regards
ooi
__._,_.___ Posted by: Jim Dirkes <Jim@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups..yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |