Thank you Julien for your quick answer, I have input 0.0001125 m3/s corresponding at ca 25 person CO2 generation rate assuming the zone is occupied between 07:50-13:30 and 14:30-16:10. Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s] output corresponds to the input value described above (0.0001125 m3/s). While Zone Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s] increases over time. I don’t understand
why this output increases over time. The zone also has an effective air leakage area of 25 cm2 and a ventilation rate of 600 m3/hr over the occupied time. a From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Hello, What did you input for the object in question? It generates Co2 for a zone based on a carbon generation design rate multiplied by a schedule. Cf I/O reference guide
https://bigladdersoftware.com/epx/docs/9-2/input-output-reference/group-internal-gains-people-lights-other.html#zonecontaminantsourceandsinkcarbondioxide So if you put something non zero in there, it's normal you're seeing this. Julien -- Sent from a mobile device, please excuse the brevity. Julien Marrec, EBCP, BPI MFBA Owner Direct: +33 6 95 14 42 13 Website: www.effibem.com On Mar 10, 2020, at 17:42, "Belleri Annamaria
annamaria.belleri@xxxxxxxxx [EnergyPlus_Support]" <energyplus_support@xxxxxxxxxxxxxxx> wrote:
__._,_.___ Posted by: Belleri Annamaria <annamaria.belleri@xxxxxxxxx> EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The EnergyPlus web site is found at: http://www.energyplus.net/ The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |