RE: [EnergyPlus_Support] ZoneContaminantSourceAndSink:CarbonDioxide outputs





Thank you Julien for your quick answer,

I have input 0.0001125 m3/s corresponding at ca 25 person CO2 generation rate assuming the zone is occupied between 07:50-13:30 and 14:30-16:10.

Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s] output corresponds to the input value described above (0.0001125 m3/s). While Zone Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s] increases over time. I don’t understand why this output increases over time.

The zone also has an effective air leakage area of 25 cm2 and a ventilation rate of 600 m3/hr over the occupied time.

a

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx <EnergyPlus_Support@xxxxxxxxxxxxxxx>
Sent: Wednesday, March 11, 2020 7:32 AM
To: energyplus_support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] ZoneContaminantSourceAndSink:CarbonDioxide outputs

 

 

Hello,

What did you input for the object in question? It generates Co2 for a zone based on a carbon generation design rate multiplied by a schedule. Cf I/O reference guide https://bigladdersoftware.com/epx/docs/9-2/input-output-reference/group-internal-gains-people-lights-other.html#zonecontaminantsourceandsinkcarbondioxide

So if you put something non zero in there, it's normal you're seeing this.

Julien

--

Sent from a mobile device, please excuse the brevity.

Julien Marrec, EBCP, BPI MFBA

Owner

Direct: +33 6 95 14 42 13

Website: www.effibem.com

LinkedIn (en) | (fr)

On Mar 10, 2020, at 17:42, "Belleri Annamaria annamaria.belleri@xxxxxxxxx [EnergyPlus_Support]" <energyplus_support@xxxxxxxxxxxxxxx> wrote:

 

Dear group members,

I am modelling CO2 generated by people within a thermal zone through the ZoneContaminantSourceAndSink:CarbonDioxide. I have set the carbon dioxide generation rate as 0 in people object and I have no electric equipment generating carbon dioxide in my model.

According to the description in the input/output reference, I would expect that the following two outputs report same amount of generated CO2:

  • Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s]
  • Zone Contaminant Source or Sink CO2 Gain Volume Flow Rate [m3/s]

However Zone Contaminant Source or Sink CO2 Gain Volume Flow Rate reports higher CO2 gains compared to the first output mentioned. Here is a plot comparing both outputs:

 

Could you please explain that?

Thank you

Kind regards

 

 

 

 

 

Annamaria Belleri, PhD

Eurac Research

 

Senior researcher

Institute for Renewable Energy 

Tel +39 0471 055 658

Fax +39 0471 055 699

annamaria.belleri@xxxxxxxxx

 

Via A. Volta 13/A

39100 Bozen/Bolzano

 

Legal Seat

Drususallee/Viale Druso 1

I-39100 Bozen/Bolzano

www.eurac.edu

 

subscribe to our newsletter

Twitter l Facebook l Youtube l LinkedIn

 

eurac_red_4c_UP_pos - Copy

 

According to regulation (EU) 2016/679 this transmission is intended only for the use of the addressee and may contain confidential information. If you receive this transmission in error, please notify the sender immediately by email and delete all copies of this message and any attachments.

Diese Nachricht ist im Sinne der Verordnung (EU) 2016/679 ausschließlich für den Adressaten bestimmt und kann vertrauliche Informationen enthalten. Sollten Sie diese Nachricht irrtümlich erhalten haben, bitten wir Sie, den Absender darüber unverzüglich per E-Mail in Kenntnis zu setzen sowie die Nachricht und etwaige Kopien und Anlagen zu vernichten.

Ai sensi del Regolamento UE 679/2016 questo messaggio è ad uso esclusivo del destinatario e può contenere informazioni riservate. Qualora Le fosse pervenuto per errore, Le chiediamo gentilmente di comunicarcelo immediatamente via e-mail ed eliminare qualsiasi copia e allegato.

 



__._,_.___

Posted by: Belleri Annamaria <annamaria.belleri@xxxxxxxxx>


EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The EnergyPlus web site is found at:
http://www.energyplus.net/

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the &quot;search&quot; button.





__,_._,___