I think I found a bug with the ERV feature in eQuest related to
temperature control.  My input is as follows:
 
   RECOVER-EXHAUST = YES
   ERV-RECOVER-TYPE = ENTHALPY-WHEEL
   ERV-SENSIBLE-EFF = 0.75
   ERV-LATENT-EFF = 0.75
   ERV-RUN-CTRL = OA-EXHAUST-DT
   ERV-TEMP-CTRL = MIXED-AIR-RESET
   ERV-CAP-CTRL = MODULATE-HX
   ERV-HX-KW =   0.207
   ERV-FANS = HVAC-SUPPLY/RETURN 
   ERV-OA-STATIC =    0.5
   ERV-EXH-STATIC = 0.5
   ERV-FROST-CTRL = USE-CAP-CTRL
 
The system shows heating savings as expected, and cooling savings during
summer periods, but during winter there is a large cooling penalty.
Hourly reports show an unexpected cooling load during winter night mode
operation.  If I set ERV-OA-STATIC to zero, that cooling load goes away.
 
If I change to a fan located in the ERV, the unexpected cooling load is
still absent:
 
  ERV-FANS = SELF-CONTAINED
  ERV-EXH-KW/FLOW = 0.002
 
Thus, it appears that the heat gain due to friction in the heat wheel is
not taken into account for the OA setpoint during night mode when
ERV-FANS = HVAC-SUPPLY/RETURN.  Has anyone else seen this problem?
 
The SELF-CONTAINED option appears to be a work-around, but it is not as
convenient for add-on heat wheels.
 
 
Thanks,
Doug Maddox, PE
THE WEIDT GROUP
  
5800 Baker Road
Minnetonka, MN 55345
T 802-262-1033
F 952.938.1480
www.twgi.com <blocked::http://www.twgi.com/> 
DougM at twgi.com <blocked::mailto:DougM at twgi.com> 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080716/1c81a10f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1223 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20080716/1c81a10f/attachment.gif>
    
    
More information about the Equest-users
mailing list