[Equest-users] Multiple HVAC systems in a single zone
Aulbach, John
jaulbach at nexant.com
Wed Nov 5 14:24:02 PST 2008
Rishi:
In general, eQuest (DOE-2) cannot model two systems in one space,
regardless if they ran at serrate times. I was thinking you could
perform the ventilation with gas boiler heat by a Unit Ventilator
(allows outside air introduction), then try the floor heating with
baseboard radiation (baseboards are allowed in many systems). However,
you cannot assign any geothermal source to baseboard heating. You MAY
want to make the baseboards electric in the model, then somehow
translate the needed load for this system into what the geothermal can
contribute, and what it can't.
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com
.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Poddar,
Rishi
Sent: Wednesday, November 05, 2008 2:06 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Multiple HVAC systems in a single zone
To all the knowledgeable eQuest users,
I am working on a design for an institutional building. Each room in the
building is its own zone. The rooms will have in floor heating connected
to a geothermal loop as well as a forced air system which will primarily
provide the required ventilation, but also heating from a supplemental
gas boiler. The core of the building will only be serviced by the forced
air system. I believe this can be done in eQUEST but I am not sure how.
The main question, is it possible to define two HVAC systems for a
single zone? Two possible operation models, one system operates at
certain times of the day, the other works at different times of the day.
The other operation model is one system works up to a certain percentage
of the requirement, and the second system meets the remaining demand. I
believe "equipment controls" can handle this, but I'm not sure how to
set it up.
Sincerely,
Rishi Poddar
Project Development Specialist
Ameresco Canada Inc.
************************************************************************
**************
NOTE: This e-mail may contain PRIVILEGED and CONFIDENTIAL information
and is intended only for the use of the specific individual(s) to which
it is addressed. If you are not an intended recipient of this e-mail,
you are hereby notified that any unauthorized use, dissemination or
copying of this e-mail or the information contained in it or attached to
it is strictly prohibited. If you have received this e-mail in error,
please delete it and immediately notify the person named above by reply
e-mail. Thank you.
************************************************************************
**************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20081105/6fe54095/attachment-0002.htm>
More information about the Equest-users
mailing list